I always knew heavy carbon oil fuels gave off more BTUs than lighter oil fuels. About 3 months ago I actually sat down and did the math.
 Post subject: Re: Combustion Theory 451
PostPosted: Wed Jun 22, 2016 8:21 am
You're making it tough to comment inline by posting this as a graphic...
To get the ball rolling: While it's useful to show stoich calculations with the elements separate (and presumably perfectly carbureted, etc.) the actual process of practical combustion more accurately resembles the premise of organic chemistry: first you have to break bonds in order to form new ones. In hydrocarbon fuels, you have to provide energy to separate the C-H and C-C bonds before you can do practical oxidation, and there is both energy and time involved in this (on a practical level). Here is a reference that is a bit simplistic but may be useful to people in this community who have had a lamentable lack of interest in this aspect of chemistry up to now:
https://www.wou.edu/las/physci/GS361/Energy_From_Fossil_Fuels.htm
There is also a natural tendency for 'atomic hydrogen' to recombine to diatomic gaseous hydrogen (and the energy represented in this bonding is surprisingly large - it's of interest in the aerospace propulsion field) rather than react directly with an oxygen molecule (which was also fundamentally diatomic as sourced in primary or secondary air)
Note that the 'hydrogen' part of most fuel combustion is not exactly invisible; it's responsible for the blue flame of natural-gas combustion. That does not change the valuable point about 'invisible products of combustion' (although I would re-introduce the Besler tube as an interesting way around some of the problems, and those tubes were demonstrated to show demonstrable improvement in practical heat uptake from gas to water in the convection section. (Can someone who has the original table showing this please provide an online copy? I have lost mine in computer changes over the years...) Something that might be useful here would be the emission spectrum of the various gases and species here, perhaps paired with the absorption characteristics of the various surfaces the emitted radiation affects...
I have tried, unsuccessfully, to figure out how the 'boiling-water' penalty applies to combustion, or how any characteristic of water at 70 degrees is supposed to be relevant to formed 'water of combustion'. In my opinion you'd have been better off looking at how the formed water 'absorbs' some of the released bond energy of combustion -- this being cognate to the 'latent heat of vaporization' at combustion temperatures, and it will not be given up in radiant, convective, or conductive heat transfer until the point of phase change, even lower than 212 F in the below-atmospheric-pressure environment of induced-draft combustion. Can you rephrase the argument a little so I understand why the boiling-water penalty is important in context?
This issue was taken up, in a different context, when the EPA tested the Donlee TurboFire XL boiler in the '80s. This used steam injection to reduce NOx generation, and "conventional wisdom" said this represented an irrecoverable loss of combustion energy. However, when an adequately long gas path is available (as was the case in the 'return' Donlee boiler, and at least theoretically for some forms of multiple-return or package boilers), and 'bottoming' recovery to a practical Rankine cycle is provided, you can get higher efficiency as well as lower-NOx benefits out of staam injection. And it follows, as for the Franco-Crosti ideas earlier in steam history, that much of the enthalpy "trapped" in the combustion water can be recovered to the Rankine cycle too...
While we are on the subject of inadequate draft for combustion: the first place I heard about this was semi-apocryphal, and had to do with the (somewhat amateur-hour, imnsho) experimentation with front ends that UP conducted in the latter half of the '30s. Supposedly at speeds over 80mph (probably with one of the 800 classes) the most efficient cutoff needed to hold high speed did not produce enough draft to keep steam production up even at the reduced mass-flow requirement. I never saw data to corroborate this, and I suspect Mr. Austin of all people knows the exact detail of this story ... and perhaps other examples of similar significance. I would like to hear further details, in detail.
PostPosted: Thu Jun 23, 2016 7:13 am
Nice article! Some remarks:
In textbooks about combustion I found this formula and used it in my thesis:
Air(lbs or kg)=11.6C+34.7(H-O/8)+4.34S
The above data for carbon and hydrogen is now extended to coal which contains oxygen and sulphur.
I have some trouble with the concept of "the boiling water penalty". Firstly because this concept is not applied to the carbon dioxide but only to hydrogen oxide. Secondly because I question the starting temperature. Theoretically this is only valid for the primary ignition.
After that the heat contained in the combustion products is sufficient to heat the oil/gas molecules to their combustion levels where they fall apart in carbon and hydrogen atoms and react with the available oxygen. My point being that the combustion product is gaseous carbon diode and water vapor right away.
Kind regards
Jos Koopmans
PostPosted: Thu Jun 23, 2016 1:10 pm
This gets way too deep for me PDQ, but I agree with the parts I can understand...
Presumably diesel (everybody's favorite subject) has more hydrogen to carbon than the good stuff. What I notice is that I have to heat the good stuff up until it's about the consistency of diesel before I can fire with it. The big difference is that it takes a lot more firing adjustments (fuel/atomizer/blower) to keep the train happy with diesel than it does with the good stuff --- is this because of the lower carbon content in diesel ??? (Please dumb down your answers a little if you would.)
As to the comment regarding not having enough draft at high speeds to keep up with steam demand, most of the time I keep the blower going when running. The exception is when steam demand is balls to the wall, then you don't need to use your blower, but you need every drop of steam. Otherwise, a little bit of blower is a hedge against getting a flashback if your fire goes out, but is also used to assist the draft when steam demand is low.
It's a balancing act --- fiddle with the knobs until the train is happy. And don't forget to pick up your check on the 10th and 25th.
Take Care & WORK SAFE
I am just an old man...
Sammy King
PostPosted: Thu Jun 23, 2016 1:57 pm
QJdriver wrote:
As to the comment regarding not having enough draft at high speeds to keep up with steam demand, most of the time I keep the blower going when running...
As this is my speciality, I would suggest another blast-cap with more orifices. This forces
the chimney to do its proper work: suck!
Kind regards
Jos Koopmans
PostPosted: Sat Jun 25, 2016 6:43 am
You pretty much answered your own question. For every nine pounds of water at 2700F, after it has passed the flame front boundary, its physical thermal energy has to be accounted for. Pretend it starts as H2O at 212F, times 9 lbs H2O/lbH2 plus latent heat (=9*970 BTU) + 212F to 2700F superheat (appx 9*141 BTU)=10,000 BTU/lbH2. Note the vapor specific heat (BTU/lb*degF) will change from 212F to 2700F, this 141 BTU/lbH2O value is an estimate. The 2700F combustion temperature is also an estimate for discussion purposes. If the fuel gas/air(oxygen) enters the boiler at 70F, the H2 + O2 increase to 212F has to be accounted for. Currently, we are not addressing what happens to the burned fuel or its physical thermal energy after it has passed the flame front boundary.
Research into the disadvantages of H2 fuel in cars will reveal that a punctured fuel tank in a collision will produce an invisible flame front that is a hazard to emergency responders. Natural gas/methane does burn with a blue flame.
I expect this is a morphed railfan legend from the 820 runaway accident in 1950. Various published accounts state the maximum speed at 120 mph. The recorded speed in the ICC Accident Report was 74 mph. Also documented in the official report were the brazed notches on the reverse quadrant limiting cutoff to 33%. This had nothing to do with drafting and everything to do with burned crankpins. Excessive high cylinder pressures at high speeds and short cutoffs caused by the inability of the residual steam to be exhausted fast enough from the cylinders, caused the grease to be wiped off the crankpins when the drivers crossed dead centers. This is a case where mechanical considerations trumped boiler efficiency considerations in the real world application. Reality gets lost in a thousand retellings.
"DESCRIPTION OF ACCIDENT
Union Pacific Railroad locomotive 820 was called to leave Cheyenne Wyo., at 6:55 p.m., August 3, 1950, and was used as front end Helper on a westbound passenger train to the top of Sherman Hill 31 miles from the Cheyenne, where it was detached from the train, turned around, and returned light to Borie, Wyo., 0.5 miles west of Cheyenne, arriving at approximately 9:00 p.m. The movements to this time were without any known unusual incident. At Borie, the locomotive was left on the eastbound track of the main line, unattended, when the engineer left to respond to a telephone message in the tower and the fireman went back to flag. After a short time, variously estimated from 5 to 10 minutes, the locomotive started to move forward and continued to increase speed on the descending main line until it struck the rear end of Union Pacific Diesel-electric locomotive unit 1149 while running at a speed of approximately 70 miles per hour. The Diesel unit was pushing a cut of cars eastward into the roundhouse lead of Old Yard in Cheyenne at the time it was struck.
The collision occurred on a double-arch stone bridge approximately 1/2 mile west of Cheyenne station. The Diesel switching unit, which was practically demolished, came to rest on its left side on the southeast bridge abutment with front end near the bottom of the bank. Locomotive 820 came to rest on its left side nearly crosswise of the tracks at the east end of the bridge with its front end wedged against the cab of the Diesel. It was also badly damaged. The tender was torn away and was lying on its left side on the bridge Extensive damage to the track on and off the bridge end to the freight cars and lading also resulted.
At Borie, Wyo., where the locomotive was stopped and left unattended, the elevation was 6560 feet, the track was tangent, and the grade eastward was 1.3 percent descending. From Borie eastward to the point of collision, approximately 9 miles, the grades were descending, varying from a maxim of 1.55 percent to 0.076 percent. At point of the collision, the track was tangent, the grade 0.1137 percent descending, and the elevation 6061 feet."
"Reverse lever, quadrant and latch were in good condition. Six teeth on quadrant just ahead of center had, been experimentally blanked by bronze welding to prevent overheating of rod pins and bushings as result of excessively short steam cutoff. When reverse lever is latched back of the welded portion of quadrant, valve motion is supposed to be on center, and when latched ahead of welded portion, at 33 percent cutoff. The setting of reverse gear could not be checked because of the damage to the Walschaert valve gear."
"Speed recorder tape, which was removed during investigation, showed the locomotive had been traveling at 45 MPH after moving one mile from Borie, 55 MPH after two miles, over 60 MPH after three miles, the speed then increased very slowly to a maximum of 74 MPH, six miles from Borie, and was maintained to point of collision. The speed recorder was removed from bracket in cab and tested on CP Speed Recorder Calibrating Machine of Chicago Pneumatic Tool Company. Slight errors were found which showed corrected speed at time of collision was probably slightly above 70 MPH."
PostPosted: Sat Jun 25, 2016 7:44 am
The coefficients are roughly the same as I quoted with the exception of the (H-O/8) expression. My first reaction is the H-O radical should really be an H-C radical representing long and/or short chain hydrocarbons (as volatiles) instead of hydroxides. If this is the case, the (/8) goes away and the H-C ratios have to be reapportioned between C and H.
JJG Koopmans wrote:
My point being that the combustion product is gaseous carbon dioxide and water vapor right away.
Carbon dioxide is a nonpolar molecule where dihydrous oxide is a polar molecule, which accounts for its liquid state at ambient temperatures. The latent heat of vaporization has to be accounted for in combustion equations. In the attached Table 71 from The Superheater Co. the 62,032-53,338 = 8,694 difference in Hydrogen heating values represents the latent heat of vaporization, 966 BTU/lb X 9 lb H2O per lb H2 burned.
PostPosted: Sat Jun 25, 2016 8:07 am
From the Cleaver-Brooks Efficiency Guide (Link) This deals with gas fuel with various H/C ratios for simplicity.
Figure 1 shows flue gas temperature vs theoretical fuel-to-steam efficiency. This table represents the maximum theoretical efficiency you can achieve at a given flue gas temperature. The table can be used as follows. If a boiler is represented to be 85% efficient firing natural gas, follow the 85% on the left to the natural gas line and down to the flue gas temperature. The result is approximately 270 deg.F. This shows the boiler would have to operate at a 270 deg. F. stack temperature to meet the 85% efficiency, or the efficiency calculation was based on an unrealistically low hydrogen content fuel. If a boiler is represented to be 85% efficient on natural gas at a 350˚ F stack temperature, check the fuel specification. A Boiler cannot operate at 85% efficiency at 350° F stack temperature when firing natural gas per Figure 1.
2. Fuel specification
The fuel specification can also have a dramatic effect on efficiency. In the case of gaseous fuels, the higher the hydrogen content, the more water vapor is formed during combustion. This water vapor uses energy as it changes phase in the combustion process. Higher water vapor losses when firing the fuel result in lower efficiency. This is one reason why fuel oil fires at higher efficiency levels than natural gas. To get an accurate efficiency calculation, a fuel specification that represents the jobsite fuel to be fired must be used. When reviewing an efficiency guarantee or calculation, check the fuel specification. Is it representative of the fuel you will use in the boiler? The representation of efficiency using fuel with low hydrogen content will not provide an accurate evaluation of your actual fuel usage. Figure 2 shows the degree to which efficiency can be affected by fuel specification. The graph indicates the effect of the hydrogen-to-carbon ratio on efficiency for five different gaseous fuels. At identical operating conditions, efficiencies can vary as much as 2.5-3.0%, based solely on the hydrogen-to-carbon ratio of the fuel. When evaluating boiler efficiency, knowing the actual fuel specification is a must.
PostPosted: Sat Jun 25, 2016 8:21 am
Kind regards
Jos Koopmans
Yes! Read the Man's Book! With less carbon in the fuel, sometimes you have to trade lower mechanical efficiency (higher back pressure) for better thermodynamic efficiency (greater suck). Efficiency is better served by resizing the exhaust nozzle such that the blower is off when running, as it should be. Use the steam in the cylinders before throwing it up the stack.
PostPosted: Sat Jun 25, 2016 9:30 am
"I expect this is a morphed railfan legend from the 820 runaway accident in 1950. Various published accounts state the maximum speed at 120 mph. The recorded speed in the ICC Accident Report was 74 mph."
What I was referring to is something radically different -- although I'm not going to say it isn't a railfan-morphed legend in the form I heard it (now probably more than 30 years ago... and I do not have either the original quote or the original source to provide.)
The discussion didn't involve mechanical damage to the running gear at all; it was purely that when the 'engine' was adjusted for minimum water rate at high running speed, the actual mass flow could be reduced below what the locomotive required for drafting to generate steam even at that lower rate. I read this before encountering the irritating lack of technical knowledge in the various Kratville books that take up the subject of UP front-end design and refinement, so I have no real idea whether this was a transient problem from one of the experiments, or was first experienced during the early high-speed testing on the UP 4-8-4s (which ISTR were the first real high-speed 4-8-4s actually tested at high sustained speeds)
It would seem that lengthening the cutoff somewhat, or using the blower judiciously (as has been reported for excursion service, perhaps in a different context) would be ways of avoiding the problem, but both those have a deleterious effect on something often even more important for modern steam than fuel consumption: water rate.
"Also documented in the official report were the brazed notches on the reverse quadrant limiting cutoff to 33%. This had nothing to do with drafting and everything to do with burned crankpins. Excessive high cylinder pressures at high speeds and short cutoffs caused by the inability of the residual steam to be exhausted fast enough from the cylinders, caused the grease to be wiped off the crankpins when the drivers crossed dead centers. This is a case where mechanical considerations trumped boiler efficiency considerations in the real world application. Reality gets lost in a thousand retellings."
This is particularly interesting because of the detail design of the intermediate 'floating bushing' in the 800-class main, with all the little cross-drilled holes supposedly acting as lubricant reservoirs but, here, acting as sinks to crash the hydrodynamic film integrity for a short - but consistent part of the main-pin circumference. I suppose this was not helped by the reduced bearing surface of the bushing due to the holes. There is also an issue of consistent peak bending moment at the root and seat of the main pins due to the high peak compression force.
These are likely to be consequences of the old 'thermodynamic desideratum' of having the tract pressure just match the inlet pressure as the valve cracks open to steam (thereby limiting pressure loss due to 'dead space' considerations). To get that approach to work right, you need reasonably reliable modulated reversible compression relief...
I don't know if I can mention SACA here without incurring displeasure of the practical engineers -- but Jay Carter has looked carefully at the 'next step' beyond Okadee compression-limiting blowoffs, and his approach should work just as nicely for a DA engine in locomotive configuration as it does for single-acting.
Be interesting to see the extent to which Timken lightweight roller-bearing mains actually 'solved' the problem of main-pin tribology during high compression. Seems logical to me that they would, but also logical that main-pin peak stresses and perhaps breakage might be enhanced where unexpectedly high compression pressures (e.g. as might be developed on throttle closing at high speed in the absence of a good bypass valve arrangement...
See the points Mr. Austin made responding to Mr. Koopmans.
PostPosted: Mon Jun 27, 2016 4:26 pm
What every oilburning fireman knows
But doesn’t know why ...
Historically, boi1er fuel was categorized as #6 or Bunker C, which was sucked out of the refinery cracking tower one nozzle aboye the asphalt drain. The difference between all grades of fuel oil is the ratio of carbon to hydrogen. The lighter the fuel oil, the greater the ratio of hydrogen atoms to carbon atoms. Inversely, the more carbon per hydrogen atoms in the fuel, the more BTUs of energy per pound of fuel liberated in combustion. Any fireman who has fired a locomotive under the same load conditions with #6, #5, #2, waste lube oil. And/or vegetable oil knows that the lighter the oil, the harder it is make steam. It is not a simple linear relationship, however.
The Fundamentals:
Heat of Combustion.
Combusting one pound of hydrogen releases 62,000 BTUs of energy.
Combusting one pound of carbon releases 14,540 BTUs of energy.
These numbers make it look simple. Everything should burn hydrogen and we get 4 times as much energy, right? Nope.
Combustion Air Requirements
To burn one pound of hydrogen requires 34 pounds of air and creates 9 pounds of waler.
To burn one pound of carbon requires 11.5 pounds of air and creates 3.67 pounds of carbon dioxide gas.
The Boiling Water Penalty
When hydrogen combusts with oxygen the product is water. When 1 pound of hydrogen burns with 8 pounds of oxygen at 70 degrees F in air, the temperature of combustion will be about 2700F, but the combustion product is water. At 70F water is a liquid. At 2700F water is a gas. To boil water to a gas absorbs energy. To boil 9 pounds of water and superheat it to 2700F requires about 10,000 BTUs. This must be subtracted from the gross combustion energy of 62,000 BTUs. The net available energy of the burning of one pound of hydrogen is about 52,000 BTUs.
The Combustion Process From the Oxygen Side:
If we are burning pure carbon in the firebox and suck in 100,000 pounds of air we release 3,793,000 BTU of heat energy.
If we are burning pure hydrogen in the firebox and suck in 100,000 pounds of air we release 1,529,000 BTU of heat energy.
What this shows is that for each pound of air consumed during combustion, we get 3793/1529 = 2.48 times more thermal energy out of each carbon-oxygen atomic bond created, than for each hydrogen-oxygen bond created.
Scientific Analysis Follows… Proceed at your own risk
Hydrogen vs. Oxygen
It is not fair to compare one pound of hydrogen to one pound of carbon. One hydrogen atom can only make one atomic bond. Each carbon atom can make 4 atomic bonds. The formation of an atomic bond gives off energy. The amount of energy released in the formation of a hydrogen-oxygen bond is not the same as the formation of a single carbon – oxygen bond. Also, to accurately understand combustion it is necessary to compare the reaction of the same number of atoms.
In chemistry this was defined by Avagadro as one MOLE = 6.02 x 10E23 atoms. The convenient way to measure the number of atoms is to base it on the atomic weight of each atom. The atomic weight of hydrogen is 1. The atomic weight of carbon is 12 and that of oxygen is 16. One pound. of hydrogen, 12 pounds of carbon and 16 pounds of oxygen all have the same number of atoms. Hydrogen can make one atomic bond, carbon 4 atomic bonds and oxygen only 2 atomic bonds.
The process of combustion is to lake atoms in their natural state, hydrogen(H2) and carbon(C) and burn/combust/oxidize them all with oxygen to create water(H2O) and carbon dioxide (CO2). When burning hydrogen and oxygen in free air, it must be taken into account that free air only contains 21 % oxygen by weight. The majority component of air is inert nitrogen.
Ignoring steam locomotive mechanical efficiency and drafting efficiency, let's just say that for a certain quantity of steam used from the boiler and out the smoke stack creates a certain quantity of vacuum in the smokebox. Since the cross sectional gas area of the tube bundle is constant, the volume of air sucked through the firebox for combustion is a function of the amount of vacuum at the front tube sheet and the cross-sectional area location of air holes into the firebox. For a coal burner. the air intakes are the area of holes in the grates (plus overfire air if equipped). For an oilburner, there may or may not be dampers, but with the dampers open the area of air openings are constant. The point to understand is that for a given steam load(throttle opening plus cutoff) the volume of combustion air through the firebox is the same, based on the geometry of the firebox air openings and has nothing to do with the BTU content of the fuel whether oil, gas or coal.
Since the draft is constant for any particular load setting, adjusting the steam generation is controlled by the amount of fuel injected into The firebox for combustion. As the carbon/hydrogen ratio decreases. the amount of BTUs released in combustion decreases. resulting in less steam being generated. It is possible, that as the carbon/hydrogen ratio decreases. a point will be reached such that insufficient heat energy will be released to maintain the steam flow required to create the vacuum that maintains the 100,000 pounds of air flow limited by the geometry of the firebox and boiler. The only solution to this situation is to create rnore draft by using more steam to allow for burning more fuel oil. The penalty for this condition is loss of thermal efficiency. More heat energy is being thrown away for the same load due only to the lower carbon/hydrogen ratio of the fuel.
Also relevant to the carbon vs. hydrogen combustion equation is that the radiant heat energy given off by each reaction is of different wavelengths. A hydrogen flame gives off no photons in the visible spectrum. The hydrogen flame is invisible. In a carbon flame, a significant part of the energy is released in the visible wavelengths of orange and yellow. This allows for radiant heat adsorption by the boiler sheets. With hydrogen giving off little radiant heat, the heat energy is transmitted by conduction to adjacent combustion gas molecules. It is a well known rule of thumb in the power plant industry that when a power plant is converted from coal to natural gas(CH4) fuel firing. the design steam output is reduced at least 10% to 30%. To promote the extra hydrogen combustion. the draft fans force more air into the combustion furnace and the transfer of heat to boiler surfaces occurs by convection as the gas flows through the boiler. The only way to maintain the original steam generating capacity, due to the lack of radiant heat energy input and increase in combustion air required, is to add more convective heating surface area to the boiler.
The Math
Carbon
14,540 BTU = 1 lb carbon
12 lb carbon = 1 mole carbon
1 mole carbon 4 mole carbon-oxygen bonds (MCOB)
1 lb carbon = 11.5 lb combustion air
Hydrogen
52,000 BTU = 1 lb hydrogen
1 lb hydrogen = 1 mole hydrogen
1 mole hydrogen = 1 mole hydrogen - oxygen bonds (MHOB)
1 lb hydrogen = 34 lb combustion air